How to determine CTs for your panel
-
- Posts: 34
- Joined: Sat May 16, 2015 6:01 pm
Re: How to determine CTs for your panel
I've been looking at this for awhile now. I started with two CT's, one per 240V leg, with the lead polarity as black/white combined on one channel.
I switched to just one CT on one leg of the circuit on the channel just to see I could get a reading. What seems to be happening is that the CT will read the correct voltage for just a short period. On the SEG site, it looks like a spike.
I've been watching the live data on the GEM config page. The numbers for Watt and amps will be zero for some minutes, then the page refreshes and I'll see normal reads for 10 seconds, then the page refreshes back to 0 again.
I switched to just one CT on one leg of the circuit on the channel just to see I could get a reading. What seems to be happening is that the CT will read the correct voltage for just a short period. On the SEG site, it looks like a spike.
I've been watching the live data on the GEM config page. The numbers for Watt and amps will be zero for some minutes, then the page refreshes and I'll see normal reads for 10 seconds, then the page refreshes back to 0 again.
-
- Posts: 12
- Joined: Wed Nov 11, 2015 11:55 pm
Re: How to determine CTs for your panel
Hello!
I read on the brultech website that for aluminum wiring I might need Micro-80 CTs instead of 40.
I opened my panel and I can see some thicker wiring for the 240v breakers and some smaller wiring for the smaller breakers. So do I need Micro-80 for all or just the upper ones, if I have aluminum wiring? Also if I do get the Micro-80 for all cables, will it actually fit my bigger aluminum cables?
Please see the attached file.
Thanks!
I read on the brultech website that for aluminum wiring I might need Micro-80 CTs instead of 40.
I opened my panel and I can see some thicker wiring for the 240v breakers and some smaller wiring for the smaller breakers. So do I need Micro-80 for all or just the upper ones, if I have aluminum wiring? Also if I do get the Micro-80 for all cables, will it actually fit my bigger aluminum cables?
Please see the attached file.
Thanks!
- Attachments
-
- 20151110_235323.jpg (1.9 MiB) Viewed 20127 times
-
- Posts: 2700
- Joined: Wed Dec 15, 2010 4:09 pm
- Location: The Bad Lands
Re: How to determine CTs for your panel
Measure some of the wires and compare them to the (inner diameter) of the CT's you are considering using.zmarty wrote:Hello!
I read on the brultech website that for aluminum wiring I might need Micro-80 CTs instead of 40.
I opened my panel and I can see some thicker wiring for the 240v breakers and some smaller wiring for the smaller breakers. So do I need Micro-80 for all or just the upper ones, if I have aluminum wiring? Also if I do get the Micro-80 for all cables, will it actually fit my bigger aluminum cables?
Please see the attached file.
Thanks!
This information is listed on the Brultech sales page.
Teken . . .
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
-
- Site Admin
- Posts: 4266
- Joined: Fri Jun 04, 2010 9:39 am
Re: How to determine CTs for your panel
Right now, in most packages, Micro-40s are replaced with Micro-80s. Your panel also has plenty of room also, so the CT size difference won't be a big deal.
You can measure as Teken said, or you could just go with the Micro-80s given the information above.
You can measure as Teken said, or you could just go with the Micro-80s given the information above.
Ben
Brultech Research Inc.
E: ben(at)brultech.com
Brultech Research Inc.
E: ben(at)brultech.com
-
- Posts: 12
- Joined: Wed Nov 11, 2015 11:55 pm
Re: How to determine CTs for your panel
Thank you both for the answers. I went with the 80s.
-
- Posts: 2
- Joined: Thu Apr 07, 2016 7:02 pm
Re: How to determine CTs for your panel
Hi, I'm going to buy your system and install it in Italy - 220v single phase. It's not clear to me if I need 2 CT for each breaker or not. Can you please clarify this aspect? thanks
-
- Site Admin
- Posts: 4266
- Joined: Fri Jun 04, 2010 9:39 am
Re: How to determine CTs for your panel
I'm almost positive it's just 1 CT as every breaker only has 1 lead. You can take a look at your panel to confirm.Fabio88 wrote:Hi, I'm going to buy your system and install it in Italy - 220v single phase. It's not clear to me if I need 2 CT for each breaker or not. Can you please clarify this aspect? thanks
Ben
Brultech Research Inc.
E: ben(at)brultech.com
Brultech Research Inc.
E: ben(at)brultech.com
-
- Posts: 2
- Joined: Thu Apr 07, 2016 7:02 pm
Re: How to determine CTs for your panel
At least in my case there are 2 wires: let's say that the load is absorbing 10A...that current will flow to the load using one of the 2 wires and will come back using the other one. I do believe that one CT is fine. And then I should just use the X2 function in the software in order to take into account that I'm running at 220v right?
Also -slightly off topic- in Italy we barely use more than 30A total in a house. Can I purchase a Mono 100 kit and have all the CT replaced with the lowest Amps ones (I believe they are 40A but not sure)?
Thanks.
Also -slightly off topic- in Italy we barely use more than 30A total in a house. Can I purchase a Mono 100 kit and have all the CT replaced with the lowest Amps ones (I believe they are 40A but not sure)?
Thanks.
-
- Site Admin
- Posts: 4266
- Joined: Fri Jun 04, 2010 9:39 am
Re: How to determine CTs for your panel
We unfortunately no longer sell 50Hz versions of the ECM-1240. You'll have to go with the GreenEye Monitor for that.Fabio88 wrote:At least in my case there are 2 wires: let's say that the load is absorbing 10A...that current will flow to the load using one of the 2 wires and will come back using the other one. I do believe that one CT is fine. And then I should just use the X2 function in the software in order to take into account that I'm running at 220v right?
Also -slightly off topic- in Italy we barely use more than 30A total in a house. Can I purchase a Mono 100 kit and have all the CT replaced with the lowest Amps ones (I believe they are 40A but not sure)?
Thanks.
I don't think you'll need the X2 option, the 2nd wire might be a neutral.
Ben
Brultech Research Inc.
E: ben(at)brultech.com
Brultech Research Inc.
E: ben(at)brultech.com