electrical panel size?

If you need help deciding on what monitor to get, which current transformers should you purchase for your panel, or anything else along these lines, start a thread here.
Post Reply
agr077
Posts: 37
Joined: Tue Jan 14, 2014 3:31 pm

electrical panel size?

Post by agr077 » Tue Jan 14, 2014 3:54 pm

Hi there,

First off, apologies if this post is in the wrong category.

I'm the process of making some decisions about the components that I need for a GEM in my house and in the process had a conversation with an electrician who I would use for the installation.

He raised an issue that I was surprised by given that I don't think I had seen it mentioned in any of the posts I have read on this forum.

The issue is with the size of my panel and that there would not be enough room inside for the CTs and wiring without exceeding the allowable capacity of 70%. He has suggested that my 200 amp Siemens panel would need to be switched out for a commercial panel tub with a 5 3/4 inch depth and 20 inch width. My current panel is roughly 12 inches wide I think. Picture is included in this post.

Is this assessment correct? What am I missing? What might he be missing?
Attachments
IMG_0006.JPG
IMG_0006.JPG (190.06 KiB) Viewed 4663 times
Teken
Posts: 2700
Joined: Wed Dec 15, 2010 4:09 pm
Location: The Bad Lands

Re: electrical panel size?

Post by Teken » Tue Jan 14, 2014 4:29 pm

I would ask him to site the NEC which he speaks of. I am not sure how this relates to adding CT's to monitor the circuit in the service panel.

I have never heard anyone speak about box fill in a service panel before. Does the service panel have a (spare) slot for the CT wires to exit?

If the answer is no, this may be what he is speaking about.
Teken . . .

My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
agr077
Posts: 37
Joined: Tue Jan 14, 2014 3:31 pm

Re: electrical panel size?

Post by agr077 » Tue Jan 14, 2014 4:50 pm

Forgot to mention that I am in Canada so NEC is not the code here. However, I would imagine the NEC and CEC are quite similar.

I don't think that he was referring for a slot for the wires to exit. He talked about the heat/temperature in the box.
Teken
Posts: 2700
Joined: Wed Dec 15, 2010 4:09 pm
Location: The Bad Lands

Re: electrical panel size?

Post by Teken » Tue Jan 14, 2014 5:37 pm

agr077 wrote:Forgot to mention that I am in Canada so NEC is not the code here. However, I would imagine the NEC and CEC are quite similar.

I don't think that he was referring for a slot for the wires to exit. He talked about the heat/temperature in the box.
Not sure what your electrician is going on about. But, installing CT's in the service panel will have no impact to generated heat or otherwise.

As long as the CT's are properly routed, secured, and do not touch any exposed channels in the service panel. Along with exiting the panel with an approved grommet.

There are no issues in the CEC with respect to the Brultech GEM.
Teken . . .

My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
ben
Site Admin
Posts: 4262
Joined: Fri Jun 04, 2010 9:39 am

Re: electrical panel size?

Post by ben » Tue Jan 14, 2014 5:50 pm

I'll ask Paul about this tomorrow, did you happen to get a picture when the panel cover was removed?

Ben
Ben
Brultech Research Inc.
E: ben(at)brultech.com
agr077
Posts: 37
Joined: Tue Jan 14, 2014 3:31 pm

Re: electrical panel size?

Post by agr077 » Tue Jan 14, 2014 6:26 pm

No i did not.
depasseg
Posts: 130
Joined: Wed Dec 11, 2013 11:10 pm

Re: electrical panel size?

Post by depasseg » Tue Jan 14, 2014 8:29 pm

Has he seen the size of the CT's and wires? Is he talking about 70% of volume of the box? I can not imagine that being an issue, since your 40 amp panel is bigger than mine.

The only references I could find (google) to 70% were related to ampacity (current) in the panel.
ben
Site Admin
Posts: 4262
Joined: Fri Jun 04, 2010 9:39 am

Re: electrical panel size?

Post by ben » Wed Jan 15, 2014 11:18 am

depasseg wrote:Has he seen the size of the CT's and wires? Is he talking about 70% of volume of the box? I can not imagine that being an issue, since your 40 amp panel is bigger than mine.

The only references I could find (google) to 70% were related to ampacity (current) in the panel.
With most installs, the CTs you'll be using throughout most of the breakers are these ones here:

http://www.brultech.com/home/store/prod ... product=45

If going with a higher accuracy, these ones:

http://www.brultech.com/home/store/prod ... roduct=115

Your electrician might be under the assumption that the size of the CTs are a lot bigger as a lot of our competitors use fairly large CTs.

Ben