OK, I think I have gotten it figured out!!
You need to connect them in series just as Ben said and Teken reminded me.
The difficult thing for me was figuring out how to do that. Now I think I know.
On a terminal block, with the two Split-60s monitoring the A/C, I used four spaces. White, Black, Black, White when it was being monitored correctly as set up in the manual.
Now, needing to connect it in series, my mistake was attempting to connect the wires together as if they were Micro-CTs, which will always be parallel either correct polarity or incorrect polarity and cancelled to zero. But parallel correct is still just the voltage of one CT, which is why it was doing what I observed and giving the reading of one CT.
So, now leaving the wires in the terminal blocks, I disconnected the two extensions going to spaces 3 and 4 of the channel. I moved the wire going to space 2 to the location where the wire to space 4 was. I then put the jumper wire between the two CT leads (one + and one -).
- DSC_9088.JPG (2.65 MiB) Viewed 13318 times
And thus the CTs are connected in series.
(Note: It is the middle four wires in the terminal block.)
And Thanks Teken for the help today!!!