Should consumption match the mains wattage?

Discuss anything which doesn't fall into the other categories here.
Post Reply
jarrod817
Posts: 1
Joined: Sun Jan 14, 2024 8:08 pm

Should consumption match the mains wattage?

Post by jarrod817 » Sun Jan 14, 2024 8:19 pm

Hello,

I have 1 GEM we have 22 breakers and all are connected to the GEM. But I naively assume that the mains consumption would match the amount consumed by all the other breakers. It seems that the system thinks I'm consuming 6K watts but only using around 1K of it.

Channel 31 is the mains, all the larger 240 breaker are channels 17-22.

Any ideas for where I should look?
Attachments
Screenshot 2024-01-14 190531.png
Screenshot 2024-01-14 190531.png (35.72 KiB) Viewed 1036 times
ben
Site Admin
Posts: 4262
Joined: Fri Jun 04, 2010 9:39 am

Re: Should consumption match the mains wattage?

Post by ben » Mon Jan 15, 2024 10:36 am

jarrod817 wrote:
Sun Jan 14, 2024 8:19 pm
Hello,

I have 1 GEM we have 22 breakers and all are connected to the GEM. But I naively assume that the mains consumption would match the amount consumed by all the other breakers. It seems that the system thinks I'm consuming 6K watts but only using around 1K of it.

Channel 31 is the mains, all the larger 240 breaker are channels 17-22.

Any ideas for where I should look?
I would first check to make sure you don't have a 240V circuit wired incorrectly. If the CTs aren't reversed then they'll cancel from eachother.

Easy way to check is to remove one set of leads from the GEM, if the value increases then reverse the leads and plug them back in.
Ben
Brultech Research Inc.
E: ben(at)brultech.com