Monitoring 220VAC

Discuss anything which doesn't fall into the other categories here.
Post Reply
Mustang65
Posts: 70
Joined: Wed Jan 21, 2015 11:17 am
Location: Central Florida

Monitoring 220VAC

Post by Mustang65 » Mon Oct 09, 2017 12:27 pm

Well, I have taken the big step!!!! I have purchased a GEM System 2 (Donut version), and it should be arriving tomorrow. Just received my shipment of DS18B20 temperature sensors this morning and a few other electronics toys. The plastic case to protect the GEM from the elements, arrives on Thursday. Here in Florida, our panels are mounted outside.

So I was looking over the documentation and had a question. The PT that is used to measure the line voltage is only connected to one of the phases. We tend to get a lot of 1/2 power outages. Yes, we lose power on only one side of the service. Can play hell on some of the equipment, but lucky for me, the AC shuts down when it only sees one phase and does not start up until they are both back in service.

So, is there an option to install a second PT and be able to monitor both phase voltages? Probably not... Wait... how about a 220 VAC PT? I would see the voltage (1/2) and could determine which phase is out, by looking at the current on the mains. PT (220VAC) used in Europe... Forget that idea....
Don

Tell me and I will forget. Show me and I may remember. Involve me and I will understand.
Benjamin Franklin
Teken
Posts: 2700
Joined: Wed Dec 15, 2010 4:09 pm
Location: The Bad Lands

Re: Monitoring 220VAC

Post by Teken » Mon Oct 09, 2017 1:54 pm

Mustang65 wrote:Well, I have taken the big step!!!! I have purchased a GEM System 2 (Donut version), and it should be arriving tomorrow. Just received my shipment of DS18B20 temperature sensors this morning and a few other electronics toys. The plastic case to protect the GEM from the elements, arrives on Thursday. Here in Florida, our panels are mounted outside.

So I was looking over the documentation and had a question. The PT that is used to measure the line voltage is only connected to one of the phases. We tend to get a lot of 1/2 power outages. Yes, we lose power on only one side of the service. Can play hell on some of the equipment, but lucky for me, the AC shuts down when it only sees one phase and does not start up until they are both back in service.

So, is there an option to install a second PT and be able to monitor both phase voltages? Probably not... Wait... how about a 220 VAC PT? I would see the voltage (1/2) and could determine which phase is out, by looking at the current on the mains. PT (220VAC) used in Europe... Forget that idea....
Hello Don,

Brultech indeed offers a 240 VAC PT if you require it. I have both in use in my home, one is using the standard 120 VAC PT on GEM 1 and GEM 2 uses the other 240 VAC PT.

But its configured to monitor 120 VAC and measures the other electrical leg of the 120 / 240 VAC split single phase electrical system in my home.

Congratulations on the new purchase and take the time to read the entire service manual. While you wait for the hardware to arrive you can print off the last few pages in the install guide which offers a blank breaker template for you to use to document each of the CT's and what loads it monitors.

Purchase some *Ideal* 44-102 label markers to help you identify and track the CT wires in the GEM's. Also, please remember the PT can not be placed on a UPS only the PSU that powers the GEM and DB should be placed on such.
Teken . . .

My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
ben
Site Admin
Posts: 4259
Joined: Fri Jun 04, 2010 9:39 am

Re: Monitoring 220VAC

Post by ben » Wed Oct 11, 2017 9:42 am

I spoke with Paul and he says it's possible you have a loose lug given the half outages. It could be in your panel, at the meter box, or at the transformer.
Ben
Brultech Research Inc.
E: ben(at)brultech.com