I've found bits and pieces of information in the forums, but it never seemed to make it to the documentation.
This is what I think I understand from what I've read - I hope someone can confirm or deny, and then maybe get it into the documentation at some point...
For an ECM-1240:
- micro-40, micro-50, and micro-80s can be used on the CH1/CH2 inputs
- Micro-CTs should be connected between COM and DUAL terminals
- Multiple Micro-CTs are wired in parallel, not series.
- A 4.99ohm resistor should also be installed between COM and DUAL
- The CT settings for Micro-40 and Micro-80 CTs should be type 169, range 4
- The CT settings for Micro-50 CTs should be type 168, range 4
And:
If a single CT is used on 1 leg of a 240V load with no neutral, then:
- The CT settings should use range 3 instead of range 4 (this doubles the values)
Is that all correct? (note: re-edited after Ben's comment below, should be correct now)
Thanks,
-eric
Last edited by
sandeen on Mon Jul 07, 2014 11:26 am, edited 2 times in total.
-
ben
- Site Admin
- Posts: 4269
- Joined: Fri Jun 04, 2010 9:39 am
Post
by ben » Mon Jul 07, 2014 10:50 am
sandeen wrote:For an ECM-1240:
- micro-40, micro-50, and micro-80s can be used on the CH1/CH2 inputs
- Micro-CTs should be connected between COM and DUAL terminals
- Multiple Micro-CTs are wired in parallel, not series.
- A 4.99ohm resistor should also be installed between COM and DUAL
- The CT settings should be type 169, range 4
And:
If a single CT is used on 1 leg of a 240V load with no neutral, then:
- The CT settings should be type 169, range 3 (this doubles the values)
Is that all correct?
The Type for Micro-50s are 168, but the rest is correct.
Ben
Ben
Brultech Research Inc.
E: ben(at)brultech.com
-
sandeen
- Posts: 41
- Joined: Fri Jan 10, 2014 3:33 pm
Post
by sandeen » Mon Jul 07, 2014 10:51 am
Thanks Ben, I'll edit the original post to avoid confusion.
It'd be great to get the updated info into the CT settings doc.