CT Orientation For GEM
I'm getting ready to do my GEM install finally, and was reading through the manual and was a little confused on the CT orientation topic and had a couple of questions:
1. Split-200 CT's - On a 200A panel, which direction does the arrow go? Arrow inwards/downwards towards the rest of the breakers or outwards/upwards towards the panel frame?
2. Micro-50 CT's - Has a "dot" on the "shiny" side, does the dot/shiny side face the breaker or away from the breaker?
3. Micro-80 CT's - No arrow or "dot" but looks the same as the Micro-50 has a "flat" and "shiny" side, does the "shiny" side face the breaker or away from the breaker?
Also I read something saying that for 240V load, on one cable/circuit/black wire the arrow/dot/shiny side faces the breaker, and the other cable/circuit/red wire the arrow/dot/shiny side faces away from the breaker towards the panel frame. Is this correct?
I know technically it does not matter which direction the "arrow/dot/shiny side" faces since you can just swap the wire connections around at the GEM, but I would prefer to setup everything the correct way the first time around so everything is the same.
Also I have 4 Split-200 CT's that I will be connecting to the 2 panels feeding my house, Can I connect all 4 Split-200's to CH1 (Panel #1 CT #1 and Panel #2 CT #1 goes to pin 1-2 on CH1 and Panel #1 CT #2 and Panel #2 CT #2 goes to pin 3-4 on CH1) or must I split them across CH1 and CH2?
Thanks
1. Split-200 CT's - On a 200A panel, which direction does the arrow go? Arrow inwards/downwards towards the rest of the breakers or outwards/upwards towards the panel frame?
2. Micro-50 CT's - Has a "dot" on the "shiny" side, does the dot/shiny side face the breaker or away from the breaker?
3. Micro-80 CT's - No arrow or "dot" but looks the same as the Micro-50 has a "flat" and "shiny" side, does the "shiny" side face the breaker or away from the breaker?
Also I read something saying that for 240V load, on one cable/circuit/black wire the arrow/dot/shiny side faces the breaker, and the other cable/circuit/red wire the arrow/dot/shiny side faces away from the breaker towards the panel frame. Is this correct?
I know technically it does not matter which direction the "arrow/dot/shiny side" faces since you can just swap the wire connections around at the GEM, but I would prefer to setup everything the correct way the first time around so everything is the same.
Also I have 4 Split-200 CT's that I will be connecting to the 2 panels feeding my house, Can I connect all 4 Split-200's to CH1 (Panel #1 CT #1 and Panel #2 CT #1 goes to pin 1-2 on CH1 and Panel #1 CT #2 and Panel #2 CT #2 goes to pin 3-4 on CH1) or must I split them across CH1 and CH2?
Thanks
GEM + WiFi & Ethernet Module / DashBox + TL-WN722N
4 x Split-200 CT's / 60 x Micro-50 CT's / 8 x Micro-80 CT's
Current 2014-03-31: GEM COM v2.58 / GEM ENG v1.47 / DB Dashboard v4.1.5F1
Previous: GEM COM v2.57 / GEM ENG v1.47 / DB Dashboard v4.1.5B
4 x Split-200 CT's / 60 x Micro-50 CT's / 8 x Micro-80 CT's
Current 2014-03-31: GEM COM v2.58 / GEM ENG v1.47 / DB Dashboard v4.1.5F1
Previous: GEM COM v2.57 / GEM ENG v1.47 / DB Dashboard v4.1.5B
-
- Site Admin
- Posts: 4269
- Joined: Fri Jun 04, 2010 9:39 am
Re: CT Orientation For GEM
Opposing eachother, one pointing up and one pointing down.OzTechGeek wrote:I'm getting ready to do my GEM install finally, and was reading through the manual and was a little confused on the CT orientation topic and had a couple of questions:
1. Split-200 CT's - On a 200A panel, which direction does the arrow go? Arrow inwards/downwards towards the rest of the breakers or outwards/upwards towards the panel frame?
Only really need to worry about orientation when installing 2 CTs onto one channel. 240V circuit CTs must face opposite directions, 120V CTs must face the same direction. It's so they don't cancel from each other.OzTechGeek wrote: 2. Micro-50 CT's - Has a "dot" on the "shiny" side, does the dot/shiny side face the breaker or away from the breaker?
3. Micro-80 CT's - No arrow or "dot" but looks the same as the Micro-50 has a "flat" and "shiny" side, does the "shiny" side face the breaker or away from the breaker?
You'll have to put them in series, so for example:OzTechGeek wrote:Also I have 4 Split-200 CT's that I will be connecting to the 2 panels feeding my house, Can I connect all 4 Split-200's to CH1 (Panel #1 CT #1 and Panel #2 CT #1 goes to pin 1-2 on CH1 and Panel #1 CT #2 and Panel #2 CT #2 goes to pin 3-4 on CH1) or must I split them across CH1 and CH2
CT1 lead 1 into Port 1, CT1 lead 2 and CT2 lead 1 twisted together, CT2 lead 2 into Port 2.
CT3 lead 1 into Port 3, CT3 lead 2 and CT4 lead 1 twisted together, CT4 lead 2 into Port 4.
(hard to put into words)
Ben
Ben
Brultech Research Inc.
E: ben(at)brultech.com
Brultech Research Inc.
E: ben(at)brultech.com
-
- Posts: 258
- Joined: Sun Apr 06, 2014 7:24 pm
Re: CT Orientation For GEM
Ben,
Why doesn't it say to have the split 200 CTs in opposite directions anywhere that I could find? Have you thought about doing a quick start, I have to say I found the installation of just the 2 x 200 Split CTs and setting up the software VERY confusing.
Alex
Why doesn't it say to have the split 200 CTs in opposite directions anywhere that I could find? Have you thought about doing a quick start, I have to say I found the installation of just the 2 x 200 Split CTs and setting up the software VERY confusing.
Alex
-
- Posts: 2700
- Joined: Wed Dec 15, 2010 4:09 pm
- Location: The Bad Lands
Re: CT Orientation For GEM
Hello Alex,scyto wrote:Ben,
Why doesn't it say to have the split 200 CTs in opposite directions anywhere that I could find? Have you thought about doing a quick start, I have to say I found the installation of just the 2 x 200 Split CTs and setting up the software VERY confusing.
Alex
The Split 200 amp CT is marked with an arrow which identifies the correct orientation of the CT. Even if you made a mistake in orientation all you need to do is reverse the wires at the end.
Teken . . .
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
-
- Posts: 258
- Joined: Sun Apr 06, 2014 7:24 pm
Re: CT Orientation For GEM
But that's the point they have two go in opposite directions when being used on a single channel. Your install pictures threw me because you had them in the same direction. I think it's because you put each one on a different channel.
My point was is there is so much info I struggled to comprehend it all. I think they need a better QuickStart guide. But that comes after the new web site
My point was is there is so much info I struggled to comprehend it all. I think they need a better QuickStart guide. But that comes after the new web site
-
- Posts: 2700
- Joined: Wed Dec 15, 2010 4:09 pm
- Location: The Bad Lands
Re: CT Orientation For GEM
You're absolutely correct! I don't believe there are too many people installing their primary CT's on two separate channels like I have.scyto wrote:But that's the point they have two go in opposite directions when being used on a single channel. Your install pictures threw me because you had them in the same direction. I think it's because you put each one on a different channel.
My point was is there is so much info I struggled to comprehend it all. I think they need a better QuickStart guide. But that comes after the new web site
I did this to ensure I was able to see the generated power, along with having a more granular view of which side of the home was using more power etc.
My apologies for the confusing!
Teken . . .
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
-
- Posts: 258
- Joined: Sun Apr 06, 2014 7:24 pm
Re: CT Orientation For GEM
Oh it was very sensible what you did. I already have an issue of 32 channels vs ~38 breakers so had to do some combining I guess I need ben to develop that expansion !
-
- Posts: 2700
- Joined: Wed Dec 15, 2010 4:09 pm
- Location: The Bad Lands
Re: CT Orientation For GEM
Hello Alex,scyto wrote:Oh it was very sensible what you did. I already have an issue of 32 channels vs ~38 breakers so had to do some combining I guess I need ben to develop that expansion !
If you have not added your voice to this thread please do!
http://www.brultech.com/home/community/ ... f=29&t=967
Teken . . .
My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929