Bogus current readings

Ask questions about the GEM here.
Post Reply
devin122
Posts: 2
Joined: Mon Nov 30, 2020 2:03 pm

Bogus current readings

Post by devin122 » Thu Sep 02, 2021 10:52 pm

Testing out my new install. When the dryer kicks on it causes all channels to read >150A. Removing one of the CTs and setting the channel to 240 causes everything to settle back down. Is this expected behavior? I'm assuming the issue has something to do with saturating the ADC, and the solution is to upgrade to larger CTs.
Image

PS: Using a micro-40, and load appears to be ~30A
ben
Site Admin
Posts: 4262
Joined: Fri Jun 04, 2010 9:39 am

Re: Bogus current readings

Post by ben » Fri Sep 03, 2021 9:17 am

devin122 wrote:
Thu Sep 02, 2021 10:52 pm
Testing out my new install. When the dryer kicks on it causes all channels to read >150A. Removing one of the CTs and setting the channel to 240 causes everything to settle back down. Is this expected behavior? I'm assuming the issue has something to do with saturating the ADC, and the solution is to upgrade to larger CTs.
Image

PS: Using a micro-40, and load appears to be ~30A
You have a Micro-40 hooked up like a Split-CT it looks like. The Splits have built-in burden resistors, the Micros use an on-board burden.

The consequence is all channels become overloaded when the circuit comes on.

Just change your dryer CTs to use Ports 2,3 instead or 1,2 or 3,4.
Ben
Brultech Research Inc.
E: ben(at)brultech.com