At 4:35pm (CST) today, my brand-new GEM has gone nuts:
EVERY channel is reporting crazy numbers, even 21-31 which have no CTs on them.
Every so often, it reverts back to "normal:"
What have I done??
Okay, I'm nuts.
Okay, I'm nuts.
- Screenshot 2021-02-22 173023.png (82.52 KiB) Viewed 3539 times
Re: Okay, I'm nuts.
Can you provide an image capture of the various settings in the GEM for review. In the interim power down the unit for ten seconds and bring it back up,
Does the problem go away?
Re: Okay, I'm nuts.
You've installed a Micro-CT like a Split-CT it looks like.
- The Micro-CTs don't have an internal burden resistor.
- Ports 1,2/3,4 on any channel are unburdened also.
Putting a Micro-CT on 1,2 or 3,4 of any channel will cause a current high enough to overload all channels.
Re: Okay, I'm nuts.
BINGO. (I think).You've installed a Micro-CT like a Split-CT it looks like.
And it was a high-current load, too, the dryer. Putting two and two together, the weirdness stopped when the dryer stopped.
Is my mistake likely to have damaged the GEM?Putting a Micro-CT on 1,2 or 3,4 of any channel will cause a current high enough to overload all channels.
Re: Okay, I'm nuts.
No damage should come from that, it's still very low amperage.TonyPh12345 wrote: ↑Tue Feb 23, 2021 11:55 amBINGO. (I think).You've installed a Micro-CT like a Split-CT it looks like.