Post by pehon » Wed May 10, 2017 7:08 am

Hello!

I have *three* water meter with pulse counter output. One is connected to Pulse counter #3 and works flawlessly.

Is it possible to use Pulse counter #1+2 (DC pulse) in addition to the dry-contact counter 3+4?

Can I use the GEM +5V DC to get the pulse from to the water meter with this wiring:

Pulse counter #1 - -> water meter-> GEM +5V -> Pulse counter #1 +

Thanks,
Peter
ben
Site Admin
Posts: 4254
Joined: Fri Jun 04, 2010 9:39 am

Re: How to use more than two dry-contact pulse counters?

Post by ben » Wed May 10, 2017 9:53 am

You can, use the attached diagram as reference.
Pulse input diagram 2.png
Pulse input diagram 2.png (45.48 KiB) Viewed 1389 times
Ben
Brultech Research Inc.
E: ben(at)brultech.com
pehon
Posts: 6
Joined: Fri Sep 16, 2011 8:47 am

Re: How to use more than two dry-contact pulse counters?

Post by pehon » Wed May 10, 2017 12:15 pm

Gorgeous Ben, thanks a lot!