slit CT 200 giving wrong reading

Posted: Tue May 05, 2015 4:44 pm
by nbarnard
I just recently setup my GEM and DB and am getting the wrong readings off one of my two CT-200s. One is correct (measured against my fluke clamp meter), other is reading consistently 56.2% low. Both are configured the same in GEM Channels.

Thanks,
Nathan

Re: slit CT 200 giving wrong reading

Posted: Tue May 05, 2015 4:52 pm
by Teken
nbarnard wrote:I just recently setup my GEM and DB and am getting the wrong readings off one of my two CT-200s. One is correct (measured against my fluke clamp meter), other is reading consistently 56.2% low. Both are configured the same in GEM Channels.

Thanks,
Nathan
Hello Nathan,

1. Is the 200 split CT monitoring a 240 circuit?
2. Are each CT's inserted into their (own) GEM channel or wired together?
3. What is the reference load you're measuring?
4. Please post up some of the CT settings in the GEM's advanced tab here for review.
5. If you review the power readings in the GEM's set up page are they correct vs the DB?

Re: slit CT 200 giving wrong reading

Posted: Tue May 05, 2015 5:41 pm
by nbarnard
Lol, I had it wired as a type 2 instead of type 1 CT. It works fine now.

Re: slit CT 200 giving wrong reading

Posted: Tue May 05, 2015 5:52 pm
by Teken
nbarnard wrote:Lol, I had it wired as a type 2 instead of type 1 CT. It works fine now.
Ha . . . :lol: Glad its all sorted out!