Ask questions about the GEM here.
Post Reply
peppersass
Posts: 107
Joined: Wed Oct 01, 2014 6:45 am

Currrent for small loads incorrect in Live Data

Post by peppersass » Sat Oct 25, 2014 8:22 pm

Adding to my report on the repeated current display for channels 17-32, it looks like the current for small loads on channels 1-16 is off by an order of magnitude.

For example, a zero-watt load (breaker off) shows 0.06A. Because the wattage is computed as 1 Watt, I suspect that's really 0.006A. More detail in my post here.
Teken
Posts: 2700
Joined: Wed Dec 15, 2010 4:09 pm
Location: The Bad Lands

Re: Currrent for small loads incorrect in Live Data

Post by Teken » Sat Oct 25, 2014 11:28 pm

3.18 firmware should resolve the current issue on channels 17-32 when its released.


Encrypted By: Phoenix Security Solutions
Teken . . .

My ongoing projects thread: http://www.brultech.com/community/viewt ... ?f=2&t=929
Buy me a cup of coffee: https://www.paypal.me/Teken https://gfinotify.com/ Discount Code: PC10
ben
Site Admin
Posts: 4266
Joined: Fri Jun 04, 2010 9:39 am

Re: Currrent for small loads incorrect in Live Data

Post by ben » Mon Oct 27, 2014 9:34 am

peppersass wrote:Adding to my report on the repeated current display for channels 17-32, it looks like the current for small loads on channels 1-16 is off by an order of magnitude.

For example, a zero-watt load (breaker off) shows 0.06A. Because the wattage is computed as 1 Watt, I suspect that's really 0.006A. More detail in my post here.
It's likely picking up a small amount of noise. Tekens suggestions in the other thread covers the ways you can try to reduce/eliminate the noise.
Ben
Brultech Research Inc.
E: ben(at)brultech.com